I have an year old Onan 10K generator and a MasterVolt inverter issue.
On shore power the inverter works perfectly but on generator power the inverter start a 2 minute cycle over and over again. It starts out Bulk charging for 2 minutes (normal) and the charger shuts off for 2 minutes and then back to normal for 2 minutes.
MasterVolt states that my generator frequency wave is close but not perfectly clean and I need to filter the power.
Generator company has checked unit twice and all is normal.
Has anyone heard of this before?
What kind of filter do I add? UPS??
Is it the inverter or my generator?
What can I do?
Thanks
Rick
-
It looks like your talking about a CONVERTER,, or possibly an inverter/ converter.. An inverter changes 12VDC to 120 V AC .>>>Dan
-
Yes, I have a 4 AGM batteries that supply my outlets with 120 outlets once the inverter does it magic.
-
Does it have a battery temperature sensor? my Magnum went crazy and Magnum sent me a new battery sensor to solve the problem
-
Yes has battery sensor.
The Inverter tech checked all settings and wires for any errors - none.
-
Get a "kill-o-watt" off Amazon, and check the hertz of your generator.
Generators don't make "dirty" power, that phrase is reserved for old, choppy, modified wave inverters.
Curious what the generator voltage is doing when the device in question is getting messed up?
Happy coaching!
Buswarrior
-
thanks
-
60 Hertz
-
It don't get any better than that,, does the generator bogg down a bit when under load ?? >>>Dan
-
The RPMs never change on it
-
That means your frequency never changes and that's a good thing.>>>Dan
-
Is it possible that the transfer switch is flaky, and not passing clean power to the inverter/charger? Can you temporarily wire around the xfer switch?
-
I have a manual transfer box that I turn to left for shore power or right to generator power.
Should I bypass this? Could the contacts be corroded?
Thanks
Rick
-
I have a manual transfer box that I turn to left for shore power or right to generator power.
Should I bypass this? Could the contacts be corroded?
Thanks
Rick
Rather than bypass, you might confirm that all the terminals are fully seated and tight, even the ones on the bottom. There will likely be 9 terminals in all (L1, L2, and Neutral for each Generator, Shore Power, Line Out to Breakers).
The terminals can get loose over time and the result is often what you're describing. When you test them for being tight, be sure to give them a good crank - they can stick in place after a few years and you'll think they're tight, but another 1/4 or 1/2 turn might be possible once they break free.
-
thank you for that help.
-
Also generator may not be grounded properly.
-
Thanks
-
Is the generator a QD 10000 Onan ?
-
Richard K. What is the model # of your Master volt inverter?
-
Inverter MasterVolt 12V2000W-10A 120V
Generator ON10.0HDKCA-11506-RP
Does that help
-
I looked at your initial post again and see that they mentioned the generator's frequency wave was not clean. I'm wondering if instead of a sine wave your generator is producing spikes somewhere in the wave. The frequency can be spot on at 60 hz and the wave pattern itself can still contain spikes or odd shapes.
Not sure how it works exactly, but if your generator uses brushes and copper commutator, I'd imagine that a little buildup in the wrong place could create spikes in the wave pattern. If the generator people are measuring the voltage and freq, they wouldn't necessary notice spikes in the wave pattern or oddly shaped waves.
Not sure if the inverter/charger is sensitive enough to the wave pattern to detect this, but that does sound like it could the kind of thing they're talking about.
-
They attached an special meter/scope (I can't remember how to spell it) it showed the wave length and it was choppy not smooth. They double checked the scope by trying another power source and the line was smooth on the second power supply.
I'm going to attach an UPS rack to the inverter to see if that correct the issue.
What do you think?
-
They probably used an oscilloscope.
If you have an access cover which allows inspection of the brushes and commutator(s) it would be worthwhile to take a look and see if there are any obvious problems.
-
That is a pure sine generator with electronic controls if the generator is malfunctioning it will throw a code he can read all he has to do is hold the stop button down and it will display any codes
-
we two different generator company checked generator
The inverter place checked it also
No codes
connections good
the scope shown choppy wave line compared to smooth on Commerial power
thanks for helping